Hi all,
I am working on a project in which 25/31.5 MVA transformers are supposed to be protected by fire water spray system and it will be controlled by Air operated deluge valve. Instrument air is not available in transformer surrounding area, so we have to plan AI supply from OSBL pipe rack, which is 300 meters far from deluge valve location.
My question is " can we run AI header underground? if not, why?"
Line size 2" / 3"
Pipe material - CS Galv
Design pressure - 10 Bar
Design temp. 65 Degree C
Operating pressure - 7 Bar
Pipe length required in UG = 200 / 250 Meters
If anyone has relevant experience, please share
Regards
Rameshwar
I am working on a project in which 25/31.5 MVA transformers are supposed to be protected by fire water spray system and it will be controlled by Air operated deluge valve. Instrument air is not available in transformer surrounding area, so we have to plan AI supply from OSBL pipe rack, which is 300 meters far from deluge valve location.
My question is " can we run AI header underground? if not, why?"
Line size 2" / 3"
Pipe material - CS Galv
Design pressure - 10 Bar
Design temp. 65 Degree C
Operating pressure - 7 Bar
Pipe length required in UG = 200 / 250 Meters
If anyone has relevant experience, please share
Regards
Rameshwar
Please Log in or Create an account to join the conversation.
- Jop
- Offline
- Moderator
Less More
- Posts: 1053
- Thank you received: 14
8 years 10 months ago #8980 by Jop
Do it once and Do it Right
Replied by Jop on topic Can we run Instrument Air in underground ??
rlpooniya,
Yes you can run an Instrument Air line underground. However there are some considerations to think about.
- Geographic location - If your plant is in an Arctic location you must deal with Permafrost.
- You will be creating a Low Point that will need to be drained. (Yes I know, Instrument Air is "Dry") There is still start-up and shutdown periods that need considerations.
Yes you can run an Instrument Air line underground. However there are some considerations to think about.
- Geographic location - If your plant is in an Arctic location you must deal with Permafrost.
- You will be creating a Low Point that will need to be drained. (Yes I know, Instrument Air is "Dry") There is still start-up and shutdown periods that need considerations.
Do it once and Do it Right
The following user(s) said Thank You: RobbC
Please Log in or Create an account to join the conversation.
- 11echo
- Offline
- Platinum Member
Less More
- Posts: 351
- Thank you received: 5
8 years 10 months ago - 8 years 10 months ago #8981 by 11echo
Replied by 11echo on topic Can we run Instrument Air in underground ??
After re-reading this, a point of interest has popped out at me ...You have a water deluge system over the top of electrical transformers!!? ...I'm not an electrical guy, but this sounds like trouble waiting to happen! ...Ask your project engineer about using halon gas system. This might require the transformers to be in a building or shed, but it would be far better then electrocuting any first responders to any fires at this point! ...My $0.02
Last edit: 8 years 10 months ago by 11echo.
The following user(s) said Thank You: rlpooniya
Please Log in or Create an account to join the conversation.
- rlpooniya
- Topic Author
- Offline
- Junior Member
Less More
- Posts: 32
- Thank you received: 0
8 years 8 months ago #9026 by rlpooniya
Replied by rlpooniya on topic Can we run Instrument Air in underground ??
Thanks JOP
@11echo,
These transformers are installed in open area with three side firewalls and one side gates. Requirement of firewater deluge system has raised by client.
@11echo,
These transformers are installed in open area with three side firewalls and one side gates. Requirement of firewater deluge system has raised by client.
Please Log in or Create an account to join the conversation.
- 11echo
- Offline
- Platinum Member
Less More
- Posts: 351
- Thank you received: 5
8 years 8 months ago #9031 by 11echo
Replied by 11echo on topic Can we run Instrument Air in underground ??
Since my last response, I have bounced this question off one of my electrical buddies and he has given me a more “refined” answer. He indicates that they can use fire water over transformers, but you need to be aware of the overall picture with this concept. The fire danger with transformer is they are filled with oil, and subject to explosions. So if there is a fire, the big problem is the oil is leaking out and feeding the fire. Transformers usually have a containment dike around them to hold this oil in the designated area (otherwise the flaming oil would run out in flat or sloped areas and cause an increase in the affected area). Now if the oil is contained, and still on fire, the water is sprayed on the oil to try to reduce the temp. to extinguish the flame. Problem there is water sinks in oil and is not as effective. Continuing the conversation with my electrical friend, he tells me the “best” way the deal with transformer fires is to use a float spray. This foam is generated with the water and is far more effective then with just plain water spray. The foam sits on top of the oil and eliminates the oil vapors the flame is feeding on.
So my advice on this subject is to talk with the engineer on this, ultimately he is responsible for the whole system! ...FYI, "if" your thinking of using threaded galvanized pipe, push to change that to H.D.P.E. pipe, at least in the buried section. ...Good Luck!
So my advice on this subject is to talk with the engineer on this, ultimately he is responsible for the whole system! ...FYI, "if" your thinking of using threaded galvanized pipe, push to change that to H.D.P.E. pipe, at least in the buried section. ...Good Luck!
The following user(s) said Thank You: rlpooniya, RobbC
Please Log in or Create an account to join the conversation.
- rlpooniya
- Topic Author
- Offline
- Junior Member
Less More
- Posts: 32
- Thank you received: 0
8 years 8 months ago #9033 by rlpooniya
Replied by rlpooniya on topic Can we run Instrument Air in underground ??
11echo,
Thanks for sharing educative conversation along with your own opinion.
Such efforts of senior members are highly appreciated....
Thanks for sharing educative conversation along with your own opinion.
Such efforts of senior members are highly appreciated....
Please Log in or Create an account to join the conversation.
Moderators: Jop
Time to create page: 0.191 seconds