Pump base out of concrete plingth, is it matters?
- mah_basha
- Topic Author
- Offline
- New Member
Please, help me soon, I am really in trouble, we are in a project for wasterwater treatment plant, I came late on this project and now implementing a design which is not mine.
however, I made a mistake, I did not check the drawings very well, which comes at the end that the pumps with bases, are out of the concrete plingth. the only easy suitable solution now is to move the pumps with bases back so that part of the steel base and the motor will be out of the conceret, is it matters so much?, to how extent can I do that?. Do I need to insist to make other concrete extension and move the pumps on it. which will take so much time and make a penality on the job. Please, help
Regards
Please Log in or Create an account to join the conversation.
- Jop
- Offline
- Moderator
- Posts: 1053
- Thank you received: 14
mah_basha.
First of all, If you are not a structural engineer, you should not do this your self. Get a structrual engineer involved.
This is what I would do.
I would treat this problem just the same as if I were replacing an old smaller pump with a new larger pump.
Chack the existing anchor bolts to see if any can be used. If so , then keep those and cut off all the others. Then I would place (two) long channel type structural members along each side the existing pump foundation (plinth). These channel members would be as heavy (thick) as possible and as deep as possible considering the dimentional relationship from the top of the existing foundation to the paving (if any) or grade. The channel members would be long enough for the new longer pump foundation. The channel members would have 4 to 6 holes along the sides and would be secured to the existing foundation with expansion anchors such as "Red Heads." Each end (pump end and the driver end) of the two side channel members would be closed off with another piece of the same sized channel. These end pieces would be welded in place to the two long pieces on each side of the pump. Drill the ends of the existing foundation to accept grouted-in reinforcing bars. Consult a structural engineer for the proper number and arrangement of the re-bar. Rig a template to locate and support the anchor bolts while the concrete cures.
After the concrete cures then remove the bolt template. For the other foundation bolts that do not match you will need to drill the existing concrete and use "Red Heads" or equal.
I hope this helps.
Do it once and Do it Right
Please Log in or Create an account to join the conversation.
- nvmani2005
- Offline
- New Member
- Posts: 3
- Thank you received: 0
Hi all
Please, help me soon, I am really in trouble, we are in a project for wasterwater treatment plant, I came late on this project and now implementing a design which is not mine.
however, I made a mistake, I did not check the drawings very well, which comes at the end that the pumps with bases, are out of the concrete plingth. the only easy suitable solution now is to move the pumps with bases back so that part of the steel base and the motor will be out of the conceret, is it matters so much?, to how extent can I do that?. Do I need to insist to make other concrete extension and move the pumps on it. which will take so much time and make a penality on the job. Please, help
Regards
It should be possible to design and provide a cantilever extension for the foundation such that entire portion of pump base and motor are within the foundation.
Please Log in or Create an account to join the conversation.
- mah_basha
- Topic Author
- Offline
- New Member
- Posts: 7
- Thank you received: 0
I am going to use your solution with some changes, first we have already the pump steel bases which is suitable for the pumps and the driver, the only problem that it comes out of the foundation, we are now thinking to put a steel bracket support to the hanged end of the base, the steel bracket shall be fixed to the plinth by anchor bolts, later we will pour concrete to the bottom of the extended part. Is this ok.
Regards
Please Log in or Create an account to join the conversation.
- EliutBB
- Offline
- New Member
- Posts: 10
- Thank you received: 0
"First of all, If you are not a structural engineer, you should not do this your self. Get a structrual engineer involved."
It really pisses me off (this is where I get rude) when people take everything on their hands even when they are not completly sure of what they are doing. How do you know if the underground is solid? A lot of people just think that in order to make a foundation you just have pour and pour indiscrimante amounts of concrete, and that the more is the best, that is wrong in most cases, when the "friatic mantle" (is that the right translation?) is too high your trenches and foundations might float or sink.
Again Im sorry, and please dont take this personaly, but that is not professional behaviour.
I truly hope you sove your problem I'v been there.
Cheers!
Eliut