Pipeline to Pipeline spacing

  • AbhijitN
  • AbhijitN's Avatar Topic Author
  • Offline
  • Elite Member
  • Elite Member
More
10 years 3 months ago - 10 years 3 months ago #6973 by AbhijitN
Replied by AbhijitN on topic Re: Pipeline to Pipeline spacing
Thanks for the inputs. It is above ground pipes running on sleepers. I have considered 1m clear distance between the pipes. I think it would be reasonable......

Please Log in or Create an account to join the conversation.

More
10 years 3 months ago - 10 years 3 months ago #6977 by rlpooniya
Replied by rlpooniya on topic Re: Pipeline to Pipeline spacing
I think 1 M clearance between two above ground pipelines is more than enough. Keep closer..... 300mm cleareance is enough

Please Log in or Create an account to join the conversation.

More
10 years 3 months ago - 10 years 3 months ago #6978 by 11echo
Replied by 11echo on topic Re: Pipeline to Pipeline spacing
Next 2 questions ...What class piping is this? ..AND what is the temp.?

Please Log in or Create an account to join the conversation.

  • AbhijitN
  • AbhijitN's Avatar Topic Author
  • Offline
  • Elite Member
  • Elite Member
More
10 years 3 months ago - 10 years 3 months ago #6980 by AbhijitN
Replied by AbhijitN on topic Re: Pipeline to Pipeline spacing
!11Echo- it is 600# LTCS pipes carrying natural gas to customers. temp--15 deg C

Please Log in or Create an account to join the conversation.

More
10 years 3 months ago - 10 years 3 months ago #6981 by 11echo
Replied by 11echo on topic Re: Pipeline to Pipeline spacing
What is the thickness of the insulation on these lines?

Please Log in or Create an account to join the conversation.

  • AbhijitN
  • AbhijitN's Avatar Topic Author
  • Offline
  • Elite Member
  • Elite Member
More
10 years 3 months ago - 10 years 3 months ago #6982 by AbhijitN
Replied by AbhijitN on topic Re: Pipeline to Pipeline spacing
Sir, these are uninsulated lines

Please Log in or Create an account to join the conversation.