Flanged valve should be used (for maintenance purpose) irrespective of size & service at : 1) At point of insulation break (generally at valves) 2) At bypass 3) At point of spec break viz. change in rating , corrosion allowance , change in piping material , etc. 4) Where spectacle blind is provided close to valve Pl. give info about it & clear my doubts regarding this.
Thanks.
The answer to your question is both "Yes" and "No"!
"Flanged valve should be used for maintenance purpose irrespective of size & service at: " Yes, if the Line class and the size is flanged. No if the size is too small to be flanged (Screwed or Socket-Weld).
1) At point of insulation break (generally at valves) Same answer applies here.
2) At bypass Same answer applies here.
3) At point of spec break viz. change in rating , corrosion allowance , change in piping material, etc. Same answer applies here.
4) Where spectacle blind is provided close to valve. Same answer applies here. If you are putting in a Spec Blind in a small line (2" /50mm or smaller) you keep the screwed or socket-weld valve and only add a pair of flanges not a more expensive flanged valve.
Pl. give info about it & clear my doubts regarding this. I hope this will help.
The answer to your question is both "Yes" and "No"!
"Flanged valve should be used for maintenance purpose irrespective of size & service at: " Yes, if the Line class and the size is flanged. No if the size is too small to be flanged (Screwed or Socket-Weld).
1) At point of insulation break (generally at valves) Same answer applies here.
2) At bypass Same answer applies here.
3) At point of spec break viz. change in rating , corrosion allowance , change in piping material, etc. Same answer applies here.
4) Where spectacle blind is provided close to valve. Same answer applies here. If you are putting in a Spec Blind in a small line (2" /50mm or smaller) you keep the screwed or socket-weld valve and only add a pair of flanges not a more expensive flanged valve.
Pl. give info about it & clear my doubts regarding this. I hope this will help.