Here’s the deal. I assume you are in Alberta by your question.
Go to ERCB directive 060 page 58/59 and it will answer some of your questions. Then go to API 521 for the rest.
The flare needs to be 50m from storage tanks (flameable liquids/vapours), 50m from wells and 25m from process equip. The knock-out is down near the flare out of the radiation zone of the stack.
If I can find API 521 I will see if I can add more.