  • #5502
    kulsingh_02
    Participant

    Dear Please somebody tell me in loop of crued oil line that….

    Is it necessary to install a drain and vent connection in every loop which is at 60M distance….please give me detail…

    #7013
    Abhijit N
    Participant

    Hi all,

    Correct me if I am wrong.

    Lines are tested together with equipment connected. Which also means, the line which is starting with vessel A to vessel B may not have hydrotest vent & drains as the connected equipment will have it & can be used for the required purpose.

    Looking forward to any correction as per the discussion we are having on this topic in this forum.

    Jop-Pls help.

    #7015
    James Pennock
    Participant

    Abhijit, You wrote:
    Lines are tested together with equipment connected. Which also means, the line which is starting with vessel A to vessel B may not have hydrotest vent & drains as the connected equipment will have it & can be used for the required purpose.

    So let’s consider the situation. “Lines are tested with equipment connected” This means the lines AND the equipment will be tested together. Correct? If this is correct, then there may or may not be any high points or low points in the piping. If there are no high points or low points in the piping then you do not need vents or drains in the piping. This means that the equipment on the high end must have a way to vent out any air in the system. It also means the equipment on the low end must have a way to drain out the hydrotest fluid. This brings us to the equipment. Do they each really have a way to vent and drain the system. Do they also have a way to fill the system?

    – Are you really going to test through the equipment?
    – If you are not going to test through the equipment then how are you going to isolate the piping from the equipment?
    – How are you going to fill the piping with hydrotest fluid?
    – What size are these specific lines (connected to the equipment)?

    #7024
    Abhijit N
    Participant

    Thank you for the reply Jop.

    Let me try & give you more information regarding the same though I myself is not too sure how they are going to do it.
    Pls refer to the attached sketch/iso for the line route info connecting two equipment.
    What is the ideal way of doing the hydro-test for this line? Do we need hydro test vent & drains?

    Jop Wrote-
    – Are you really going to test through the equipment?—I am not really sure about it.
    – If you are not going to test through the equipment then how are you going to isolate the piping from the equipment?–We have spec. blind at one end but nothing like it on the other end. Then I am not sure what is the means of isolating it from equip?
    – How are you going to fill the piping with hydro-test fluid?–If not the test is not together with equip. I think we need to have these High point vent / drains for sure.
    – What size are these specific lines (connected to the equipment)?–6″

    Looking forward to your feedback on above situation.

    Regards,
    Abhijit

    Attachments:
    #7026
    James Pennock
    Participant

    Abhijit,
    Thank you for the sketch. It helps a lot.
    The way I see things, you have two options:
    Option #1 – Hydrotest the piping on the ground before you install the piping. Get two Blind Flanges and install a valved connection (hole in the BF, O-Let fitting , Nipple and valve) in each Blind Flange. Arrange the piping on the ground so there is only one high point and one low point. Install the valved blind flanges and fill the piping with water and do the test.

    Option #2 – Install two small valved outlet connections minimum distance from each end flange of the line. Install the line complete with the Spec Blinds. Use the two new branch connections to fill the line and bleed out as much air as possible. Do the test making allowance for the fact you do not have a completely full line. After the test open the valves to drain out most of the water then open the flanges to remove the Spec Blinds and drain out the rest of the water.

    #7031
    Abhijit N
    Participant

    Option#1 sounds great with minimum changes required.
    Thank you for your response & now I do understand a bit about the way hydro-testing is done in similar situations.

    #7336
    Lino Lardizabal
    Participant

    It is not advisable to do this on the fabricator side because it will take time and effort. Hydro-testing is only done on the field. And it will also be expensive if this will be done by the fabricator, it will require additional fee.
    The contractor will have a welding inspector for the fabricated spool