- Posts: 13
- Thank you received: 0
Fixed & sliding Saddle
- Arakeri
- Topic Author
- Offline
- New Member
Less More
13 years 3 weeks ago - 13 years 3 weeks ago #8030 by Arakeri
Fixed & sliding Saddle was created by Arakeri
In horizontal vessel , how to decide which saddle will be fixed one
Please Log in or Create an account to join the conversation.
- Jop
- Offline
- Moderator
Less More
- Posts: 1053
- Thank you received: 14
13 years 3 weeks ago - 13 years 3 weeks ago #6227 by Jop
Do it once and Do it Right
Replied by Jop on topic Re: Fixed & sliding Saddle
Normally you anchor the end of the vessel closest to the pipe rack which is also the end with the pump suction nozzle and you want to minimize movement that might effect the pumps.
Do it once and Do it Right
Please Log in or Create an account to join the conversation.
- shrivallabha
- Offline
- Premium Member
Less More
- Posts: 149
- Thank you received: 0
13 years 2 weeks ago - 13 years 2 weeks ago #6228 by shrivallabha
Replied by shrivallabha on topic Re: Fixed & sliding Saddle
Few things that I'd like to add:
1. The nozzles which are connected to other equipments will benefit if you place them closer to the fixed saddle so the movement will be minimized.
2. Place unconnected items such as Pressure Temperature gauges to the moving side so you don't have to bother about the effect of movement.
1. The nozzles which are connected to other equipments will benefit if you place them closer to the fixed saddle so the movement will be minimized.
2. Place unconnected items such as Pressure Temperature gauges to the moving side so you don't have to bother about the effect of movement.
Please Log in or Create an account to join the conversation.
- Er.piping
- Offline
- Junior Member
Less More
- Posts: 36
- Thank you received: 0
11 years 3 months ago - 11 years 3 months ago #6734 by Er.piping
Replied by Er.piping on topic Re: Fixed & sliding Saddle
It is preferred to fix the end of horizontal vessel close to the pipe rack.
But in case of horizontal exchangers which is connected to U/G CWS & CWR headers,
exchanger is fixed at channel end (away from pipe rack) due to stress reasons.
But in case of horizontal exchangers which is connected to U/G CWS & CWR headers,
exchanger is fixed at channel end (away from pipe rack) due to stress reasons.
Please Log in or Create an account to join the conversation.
- 11echo
- Offline
- Platinum Member
Less More
- Posts: 351
- Thank you received: 5
11 years 3 months ago - 11 years 3 months ago #6736 by 11echo
Replied by 11echo on topic Re: Fixed & sliding Saddle
IF you’ll look at the exchangers you’ll see the connections are at one end, this is the end you’d want to anchor. By anchoring here you’ll eliminate the stress to the piping connecting to the exchanger by directing the thermo growth of the exchanger to the sliding end.
Please Log in or Create an account to join the conversation.
- Er.piping
- Offline
- Junior Member
Less More
- Posts: 36
- Thank you received: 0
11 years 3 months ago - 11 years 3 months ago #6737 by Er.piping
Replied by Er.piping on topic Re: Fixed & sliding Saddle
Dear 11echo,
I have followed below criteria for deciding fixed and sliding saddle for the exchanger.
Case 1: If all the lines connected to exchanger are coming from pipe rack, It is fixed at bonnet end (rack side), to avoid expansion being transferred on pipe rack.
Case 2 : If the exchanger is connected to the under ground cooling water supply and return header, then it is fixed at channel end. Since the U/G and A/G interface is treated as anchor point so thermal growth of exchanger is not allowed at channel end.
I have followed below criteria for deciding fixed and sliding saddle for the exchanger.
Case 1: If all the lines connected to exchanger are coming from pipe rack, It is fixed at bonnet end (rack side), to avoid expansion being transferred on pipe rack.
Case 2 : If the exchanger is connected to the under ground cooling water supply and return header, then it is fixed at channel end. Since the U/G and A/G interface is treated as anchor point so thermal growth of exchanger is not allowed at channel end.
Please Log in or Create an account to join the conversation.