stop check valve in vertical direction

  • imranbagdadi
  • imranbagdadi's Avatar Topic Author
  • Offline
  • New Member
  • New Member
More
10 years 7 months ago - 10 years 7 months ago #8334 by imranbagdadi
stop check valve in vertical direction was created by imranbagdadi
I am using a stop check valve (straight pattern) in 4" line, can it be install in vertical direction

Imran Bagdadi

Please Log in or Create an account to join the conversation.

More
10 years 7 months ago - 10 years 7 months ago #6877 by Jop
1. What is the direction of flow in the line?
- If the flow is down than my answer is NO! you cannot do that
- If the flow is up then my answer is maybe.

2. You must ask the manufacturer (maker) if the check valve listed in your Material Specifications will re-seat (close) if installed in the the vertical/flow up position?

Do it once and Do it Right

Please Log in or Create an account to join the conversation.

More
10 years 4 months ago - 10 years 4 months ago #5231 by 11echo
Replied by 11echo on topic Re: stop check valve in vertical direction
"In-Line" stop check valves can NOT be positioned in the vertical( www.ladishvalves.com/Portals/203 ... %20iom.pdf . ...look @ page 3 left side, half way down above red caution box). They do make right angle stop-checks that are positioned on the top of a vertical run of pipe and work properly. ALSO note the stop-checks work best in "clean" commodities!!! ...Good Luck!