Pad / Stub-in & out connections
- Sachin
- Topic Author
- Offline
- Junior Member
Less More
15 years 3 months ago - 15 years 3 months ago #7465 by Sachin
Pad / Stub-in & out connections was created by Sachin
A 10†pipe branch is taken from 12†pipe header .
Service : Cooling water
Pipe MOC : Galv CS A53 FBW/ A53 B/ API 5LB ( Galv is for small bore viz. upto 2†only )
Corrosion Alwc : 0.125â€
T & Pr : -20 F to 366 F @ 150 psig
Piping Specification requires stub - in connection for 12†x 10†.
Caeser II software requires Pad .
PDS software shows RWELD without Pad .
Pl. give the correct procedure & share info regarding pad requirement for Stub - in / out connections .
Thanks
Service : Cooling water
Pipe MOC : Galv CS A53 FBW/ A53 B/ API 5LB ( Galv is for small bore viz. upto 2†only )
Corrosion Alwc : 0.125â€
T & Pr : -20 F to 366 F @ 150 psig
Piping Specification requires stub - in connection for 12†x 10†.
Caeser II software requires Pad .
PDS software shows RWELD without Pad .
Pl. give the correct procedure & share info regarding pad requirement for Stub - in / out connections .
Thanks
Please Log in or Create an account to join the conversation.
- Jop
- Offline
- Moderator
Less More
- Posts: 1053
- Thank you received: 14
15 years 3 months ago - 15 years 3 months ago #4918 by Jop
Do it once and Do it Right
Replied by Jop on topic I would make a reinforcing
I would make a reinforcing pad out of the 12" pipe material and a minimum of 5" wide.
Do it once and Do it Right