Dear All,
Just wanted to know about the requirement of the flare line branches being called for 45 deg conections. Can that be deviated? Under what conditions it can be deviated?
"Latrolet Connection requirement in Flare Line"
Where did this requirement come from? Is this from a Client Project Design Specification?
"Can that be deviated?" Have you asked the source if there are any exceptions to it?
"Under what conditions it can be deviated?" You need to ask the source.
Flare Header connections are NOT all lateral connections. In my working life I would say that 75% (or more) were normal 90 degree connections and the balance were lateral connections. I think all of the Lateral connections were driven by Client preference.
Its usually driven by size as well.....for example:
Individual safety valve piping that has a diameter larger than half the header diameter, shall enter the header at an angle of 45 degrees in the direction of the flow in the header. Safety valve piping having a diameter less than half the header diameter shall enter the header at and angle of 90 degrees. In all cases the discharge piping shall enter the header in the top.
[i]"Its usually driven by size as well.....for example:
Individual safety valve piping that has a diameter larger than half the header diameter, shall enter the header at an angle of 45 degrees in the direction of the flow in the header. Safety valve piping having a diameter less than half the header diameter shall enter the header at and angle of 90 degrees. In all cases the discharge piping shall enter the header in the top."[/i]
Again I say this is no doubt a "Client" or "Company" preference" not an Industry Standard or Code.
kumaraba,
You need to find out where your requirement came from and if there are any exceptions to it.
You also need to question yourself as to why you are resisting lateral stub-in branches for this service.
The latrolet connection requirement might be arising from:
1. Turbulence that gets created at the header connection, which is not good from flow point of view. The discharge at fairly high velocity will create eddies and thereby add to the pressure drop.
2. Secondly, the direct impinging may result in erosion of header pipe.
I've seen these connections also at boiler stack, where the flue gas discharge connects with (vertical) stack at 45°.
One more thing that is little idiosyncratic but might be of significance. Of the two international projects I was part of, the flare connection was normal (90°) and in the domestic (mostly EIL projects), it was 45°.
And then famous quote, that is what we did in the past jobs.
Regards,
I recommend it to connect at 45^ in the direction of flare flow in header instead of 90^.
we are here talking about the safety valve. will not pop up daily basis, but only in the case when it will pop up...... it should work accurately.
why to take a chance?
impigment can creat major accident in the case of 90^ discharge enrty bacause the flow from safety valve dischange will be much higher and instantaneous.
If I talk about the project I worked in, It was the very strict (no deviation acceptable) instruction from process people to connect discharge to header at 45^ only (and not at 90^).